 heating the shop-radiant floor vs. infrared above

We are building a 30'x50' insulated pole barn. The main area will be concrete. I plan on using it for car storage, a work-shop, and the kids can play basketball there in the winter (vaulted trusses).

I want to keep it about 50-60 degrees in the winter. Should I install a propane infrared overhead tube heater, or insulate the slab and run radiant floor heating? I don't have to heat all 1500 sq ft, and thought about in-floor heat on just half, and use a thermal break to separate heated slab from unheated. But am worried about the long term cost to keep that floor heated all winter. Would it be better to just use infrared as needed when occupied? Would I just buy a hot water heater to hook up to the in-floor heat with a thermostat?






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-22-2018, 22:23 Post: 111385
hardwood



View my Photos

View my Photos  Pics
Join Date: 0000
Location: iowa
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 786
 heating the shop-radiant floor vs. infrared above

My heated shop is realitvly small 24 x 26, but if I were to do it over I'd probebly use the same system installed about 25 yrs. ago. I don't remember the exact amounts, but under the slab we put 2-3 in. of foam board then put radiant heaters just below the ceiling, (about 9 ft.). It seems to not cost a lot to keep it at about 50 degrees, and have had no matinence problems yet. Liquid heated floors are getting popular and they may have some advantages over what I did, you should check it out. I'm sure ther are folks on the board who have them and perhaps they will share their experience. Best of luck. Frank.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-23-2018, 03:18 Post: 111391
havoctec



Join Date:
Location: Minnesota
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1

3
Filter by User
 heating the shop-radiant floor vs. infrared above

If you want to keep it heated all winter then in floor is the way to go. If you just want to heat it when it is in use then radiant heat is the way to go. Our shed is 26x40 with in floor using an electric on demand hot water heater. It is on an off peak elctric meter ($.04/kw) and it costs about $300 to keep it at 50 deg. all winter.

I would stay away from the forced air gas units. JMHO.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-23-2018, 08:12 Post: 111420
pkzochow



Join Date: 0000
Location: Michigan
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 17
 heating the shop-radiant floor vs. infrared above

In floor heating would be the way to go. Do you have access to wood for heating? I have a neighbor that built a 34x60 barn and a 3,000 square foot house and is all heated off one of the outdoor wood burners, it could heat twice that with out any issues.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-24-2018, 13:39 Post: 111473
chrisscholz



Join Date: Oct 2003
Location: iowa
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 59

2
Filter by User
 heating the shop-radiant floor vs. infrared above

I thought about outdoor wood furnaces, but work too many hours to be cutting firewood.

What about the on-demand electric water heater idea? Never heard of these for in-floor heat. Wouldn't a simple gas or electric water heater be better? What is the advantage? I do want to keep my utilities low. I am still leaning towards radiant floor heating in part of the shop's floor. I assume with decent insulation that this radiant heat would help the entire shop stay 50-60 degrees.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-24-2018, 18:33 Post: 111482
havoctec



Join Date:
Location: Minnesota
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1

3
Filter by User
 heating the shop-radiant floor vs. infrared above

Yes you can use a regular gas hat water heater. Everyone that I have talked with says don't use an electric tank hot water heater. I think the problem has to do with recovery time and element longevity. I went with a tankless heater that is designed for in floor heat because we do not have anything else that is gas and didn't want an LP tank sitting beside my shed. I attach a link, hopefully it works.

If you want to heat the shed all winter I think the in floor is the most economical. followed by the radiant heat. The nice thing about radiant heat is that you can shut it off and it does not take long to warm up your building again. Not so with in floor.

If you do go with in floor I would urge you to do the whole building. You can do two seperate zones so that you don't heat the whole bilding but you will still have the capability if you want it latter. It's dang hard to get that tubing into hard concrete!!






Link:   Click Here 

Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-24-2018, 23:28 Post: 111492
daveinnh



Join Date:
Location: central NH
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1
 heating the shop-radiant floor vs. infrared above

Although we don't have a barn yet, our timber-framer provided a 1st floor radiant slab and a basement slab (for my workshop). The basement slab is insulated w/ 2" blue-board beneath; the radiant tubing and components are supplied by "Wirsbo".

You should speak to a local plumber how has done this work before, has the (radiant) tools, and is comfortable in working w/ radiant. I keep the cellar at about 61 deg. - it's cool initially, but once you start working, it becomes almost hot.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-25-2018, 04:22 Post: 111539
AnnBrush



Join Date:
Location:
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1
 heating the shop-radiant floor vs. infrared above

On demand water heaters are common in Africa. Over the whole year they are more efficient than regular tank heaters (they dont keep a reseviour of water hot). However they are very ineffiecient when actually heating water. To verify this you only need to look at the venting requirements for these units. It's kind of like the BTUS to heat a gallon of water is WAY higher for a on-demand heater vs a regular heater but then you have no BTUS needed to keep it hot so the turtle passes the hare and wins the race. In this case a tankless heater would be a disaster for heating water to provide building heat since I assume there would be a almost constant demand and therefore a constant operation of the tankless heater and subsequent efficiency loss.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-25-2018, 09:16 Post: 111542
dklopfenstein



Join Date: Jul 2004
Location: Southern Indiana
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 124
 heating the shop-radiant floor vs. infrared above

I have floor heat in my 38x44 shop and heat an apartment above it (about 1,000 square feet)with an 85% efficient boiler. In the shop below, I have four overhead doors and other windows/doors. I heat the shop to about 63 and the apartment to 72 all winter long and only have to fill-up my 500 gallon propane tank 1x per year. We like the heat and love the efficiency. You will never regret this system even though it is more $ initially. Indiana winters can be rough at times so it is a good "test area" for others.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
 02-25-2018, 14:11 Post: 111551
havoctec



Join Date:
Location: Minnesota
TractorPoint Premium Member -- 5 Tractors = Very Frequent Poster
Posts: 1

3
Filter by User
 heating the shop-radiant floor vs. infrared above

The on demand gas heaters may be less efficient but the electric units are as close to 100% efficient as you can get. There is no heat loss through a vent with electric and any heat that is lost goes into the building.






Reply to PostReply | Quote Post Reply to PostQuote Reply | Add PhotoAdd Photo




Bookmarks: Digg It | Del.icio.us |
Reply | Pop Up Window Reply | Add PhotoAdd Photo


Page [ 1 ] | 2 | | Next >>

Discussion Boards > Active Subjects > Messages as Posted > Barns and Out Buildings Forum

Thread 111378 Filter by Poster:
AnnBrush 1 | brokenarrow 1 | chrisscholz 2 | daveinnh 1 | dklopfenstein 1 | farmer 1 | hardwood 1 | havoctec 3 | pkzochow 1 |

 (advanced search)



Unanswered Questions

Gas Generator Weather Protecti
Horse Injured Polyrope Electri
Do electric fences keep out de
Any Peruvian Paso Owners Out T
gas powered post driver
My new born foal is really sic
Trailer Axle
dump trailer blueprints


Active Subjects

Gas Generator Weather Protecti
Went to see Dennis Reis this w
Signs to look for prior to lab
leg injury
Broodmare has welts all over h
Some Christmas Humor For Horse
poles in the ground vs. concre
ever thought about moving?


Hot Topics

new app owner
Some Christmas Humor For Horse
Any Peruvian Paso Owners Out T
Heating a Garage
Gas Generator Weather Protecti
Do electric fences keep out de
gas powered post driver
Trailer Axle


Featured Suppliers

Mountain Creek Labradoodles
      MountainCreekLabradoodles.com





New Forums on Gun Sport Shooting and Hunting -- BarrelPoint.com  New Forums on Horses ManePoint.com
Talk Horses at ManePoint
Hunting + Gun Sports at BarrelPoint



Most Viewed

+ Floor paint
+ The Icynene Insulation SystemŽ
+ poles in the ground vs. concrete footings with anc
+ New barn
+ Heating a Garage
+ Increasing door height to fit tractor
+ New addition for my new Tractor
+ Pole Barns and Post Holes
+ Garage Heater
+ Advice on building a shop

Most Discussion

+ New barn
+ New addition for my new Tracto
+ The Icynene Insulation SystemŽ
+ vinyl siding
+ Heating a Garage
+ Land Preparation
+ Garage Heater
+ Increasing door height to fit
+ Advice on building a shop
+ poles in the ground vs. concre

Newest Topics

+ Gas Generator Weather Protection
+ revisisting icynene insulation again
+ Building new pole barn
+ Electric/Insulation Job estimate
+ Pole Barn or stick built
+ heating the shop-radiant floor vs. infrared above
+ Pole Barn Concrete Floor
+ Gravel Compaction under Conc. Slab Floor
+ Advice on building a shop
+ finishing touches on barn
















Turbochargers for Tractors and Industrial Machines
Cab Glass for Tractors and Industrial Machines

Alternators for Tractors and Industrial Machines
Radiators for Tractors and Industrial Machines

Driveline Components for Tractors and Industrial Machines
Starter Motors for Tractors and Industrial Machines